So I tried installing the Honeywell Home RTH9585WF. Followed the directions, including shutting off the A/C breaker before working on it. As soon as it was all in place, I turned the breakers back on, and it didn't work. Machine didn't even power on. The cables were a bit bent, so I stripped them back and put them in cleanly. Still not turning on. I thought my model was defective, so I replaced it with the old thermostat, and now the old thermostat isn't receiving power either.

What are some steps to try?

The C and R wires are both present, and the Y W and G wires are the other ones there

craggy obsidian
#

Check if there is a fuse on the furnace main panel, it might be blown.

#

If you shorted something that would probably blow and you wouldn't get power anymore

fossil shoal
#

Huh, one of the furnance panel? My first look I didn't see something like that, though I did turn the only "on and off" switch I saw on and off while troubleshooting. The main one I manually flipped off during work

craggy obsidian
#

Like wherever the other end of the R/C/G/Y wires go, it should go to a circuitboard somewhere

fossil shoal
#

Yeah I traced the other end of the wires to the unit itself, they were connected, but I didn't see a breaker anywhere

craggy obsidian
#

not a breaker, but a fuse is small

#

it'll be a little blade fuse or a cylinder

#

I'm just guessing

fossil shoal
#

Huh, lemme go check again

craggy obsidian
#

like one of these

fossil shoal
#

How will I tell if that is blown?

craggy obsidian
#

with a multimeter if you've got one, or you can maybe just look at it closely and see if the wire is broken inside

#

first go see if you can find it and then worry about that afterward

#

or possibly something like this

fossil shoal
#

I can't really see anything along those lines

craggy obsidian
#

there with the 3

#

pull it straight out from the board

fossil shoal
#

Pull it off??

#

Here's a better look at it

craggy obsidian
#

it should come right out, it's just 2 blade legs in a socket

fossil shoal
#

I guess if this doesn't work I'm calling the HVAC guy anyway...

#

Lemme flip the breaker off again

craggy obsidian
fossil shoal
craggy obsidian
#

I can't really tell, there should be a very fine wire between the legs visible through the window
If it's broken, it's dead, if it's continuous, it is ok

#

Do you have any multimeter to test with?

fossil shoal
#

They don't seem to be attached... Lemme grab my multimeter

craggy obsidian
#

yeah just check the Ohms between the legs

fossil shoal
#

Wow... Yeah the fuse is toast

craggy obsidian
#

Ok, well at least you know now. Just got to get a replacement from the hardware store.

#

or get several 😁

fossil shoal
#

Why would it blow from replacing a thermostat?

#

Yeah not a bad idea

craggy obsidian
#

it would blow if one of the hot wires got shorted to ground

fossil shoal
#

I had the breaker off, or at least the one labeled "A/C"

#

Maybe I need to shut the entire house's power off next time

craggy obsidian
#

could be bad thermostat, could be miswired, could be that the lines were still hot and they accidentally touched when you were moving things around (I did this once 😭 )

fossil shoal
#

Honestly its likely the later... But I'm returning this one anyway

craggy obsidian
#

Anyway good luck. I'm assuming once you plug in the new fuse it will be back up and running

fossil shoal
#

I assume so. Nothing else makes sense

#

Thankfully its the cold season

craggy obsidian
#

you can also check for voltage on the terminals with the multimeter

fossil shoal
#

Well, I'll take the blown one to my local hardware store and see if they have it. Then check others if they don't have it

#

So using the ohms/resistance meter checks if they're connected, while the voltage sees if any power is flowing?

craggy obsidian
#

sort-of

#

I'm assuming you have 24V thermostat, so measuring the voltage between R and C should be 24VAC if there's power to the thermostat

#

in your case you'll measure 0 since there's no power

fossil shoal
#

Anything I should know of before getting a new 3 amp fuse? I'm guessing there's lots since apparently its for cars too

craggy obsidian
#

they come in a few sizes that are fairly similar looking, so just make sure it's exactly the same size

fossil shoal
#

I'll bring the dead one with me

craggy obsidian
fossil shoal
#

Are there any other considerations besides dimensions and amp rating?

craggy obsidian
#

no that's pretty much it

#

fuse is a fuse

fossil shoal
#

I'll learn electronics better someday

#

I can wire a network but I guess I can't fix a simple short

fossil shoal
#

Damn I just realized, does a simple thermostat have enough juice to kill someone?

#

I know the furnace itself probably has that

fossil shoal